C cppoly Senior Member Location New York Dec 26, 2017 #1 Are there any restrictions to mounting a receptacle at the floor level in a kitchen island or also what about inside kitchen cabinets?
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Dec 26, 2017 #2 Are these in addition to the required recs of 210.52? These can be added, but neither description will satisfy counter top rules.
C cppoly Senior Member Location New York Dec 26, 2017 #3 Yes in addition to the required outlets of 210.52. So these are OK then?
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Dec 26, 2017 #4 cppoly said: Yes in addition to the required outlets of 210.52. So these are OK then? Click to expand... Yes.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Dec 26, 2017 #5 I agree with Derek you first must comply with the required receptacles after that you're free to install additional receptacles just about anywhere that you want. The additional receptacles would still need to comply with the SABC rules.