Maybe

New member
the code says you have to ground metal faceplates. I have a handy box with a metal faceplate I was told the faceplate mounting screw was not allowed by code as a grounding means?
 
1-Who told you that?

2-And if that statement were true how on earth would you bond the metal faceplate?
 
Anybody have any problems with the practice of using a metal blank plate (handy box blank) on a plastic wall box? Or a metal octagon blank on a plastic ceiling box? (assume exposed work for both)
 
mdshunk said:
Anybody have any problems with the practice of using a metal blank plate (handy box blank) on a plastic wall box? Or a metal octagon blank on a plastic ceiling box? (assume exposed work for both)

Yes, a few times inspectors asked if we would change the blank plate to plastic since the wall box was plastic..
 
infinity said:
2-And if that statement were true how on earth would you bond the metal faceplate?

well first you would tape the wirenuts and sides of the receptacle to minimize the chance of the plate becoming energized. an AFCI would be a good idea too. Then cadweld a lug to the faceplate and run a #8 solid copper and cadweld it onto the GEC.
 
mdshunk said:
Anybody have any problems with the practice of using a metal blank plate (handy box blank) on a plastic wall box? Or a metal octagon blank on a plastic ceiling box? (assume exposed work for both)


I just drill and tap a foot lug to the back side of the plate...:grin:
 
Exception No. 1 to 517.13(A) alludes to the fact that the screw holding the cover to the receptacle is sufficient, assuming the receptacle is properly connected to an EGC.
 