Does a receptacle located near by (2 ft away) eye wash station need to be GFCI? The code only lists for commercial building only kitchen, roof top and outdoor. my take on it, this is not a kitchen sink. Any thoughts? Thanks,
Read to 210.8(B)(5)
Roger
I guess I should of asked what code cycle you are under, see Hurks post above.Roger:
210.8(B)(5) for outdoors applications. This eye wash is located indoor.
I have literally used them to rinse my eating utensils after lunch and breaks.I've used them for washing my hands many times.
That would set off alarms on a number of them that I have worked on.I have literally used them to rinse my eating utensils after lunch and breaks.
Roger
OTOH, there are those that would see them as sinks and would have a pretty good argument for their point of view IMO.That would set off alarms on a number of them that I have worked on.
Even if you do wash things in them, I don't see them as sinks and triggering a requirement for GFCIs.
OTOH, there are those that would see them as sinks and would have a pretty good argument for their point of view IMO.
Roger
Other than the ones that are installed as part of a lab sink, I have never seen one that would call a sink.
Merriam Webster said:Definition of SINK
1
c : a stationary basin connected with a drain and usually a water supply for washing and drainage
What is the reason for the GFCI sink rule?
IMO it is a sink even though I doubt that it is what the CMP had in mind.
I have seen very few that were connected to a drain, and its purpose is "rinsing", not "washing".Merriam Webster said:Definition of SINK
1
c : a stationary basin connected with a drain and usually a water supply for washing and drainage
I have seen very few that were connected to a drain, and its purpose is "rinsing", not "washing".
I just don't see how there is a safety hazard just because there non-GFCI receptacle close by.They have drains but they are not usually connected to the waste lines, they drain to the floor. The difference between rinsing and washing can be debated but they seem fairly close to me. We don't consider them sinks but we require GFCI's as if they were sinks. Seems like a minor expense for an industrial facility just to be on the safe side.
I just don't see how there is a safety hazard just because there non-GFCI receptacle close by.