ritelec Senior Member Location Jersey Feb 6, 2020 #1 Flat screen tv over electric fireplace The fire place unit is about 3' down from the tv receptacle to be installed. Heat comes out from under heater. Are there any exception to allow a receptacle to be mounted above a heater? Thank you
Flat screen tv over electric fireplace The fire place unit is about 3' down from the tv receptacle to be installed. Heat comes out from under heater. Are there any exception to allow a receptacle to be mounted above a heater? Thank you
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Feb 6, 2020 #2 Is there something in the fireplace unit instructions that prohibits a receptacle above it?
rcarroll Senior Member Location Fort Collins, Colorado Feb 6, 2020 #3 A receptacle above a fireplace probably isn't a problem, depending on the instructions. Above a baseboard heater, I've not seen any exceptions Ron
A receptacle above a fireplace probably isn't a problem, depending on the instructions. Above a baseboard heater, I've not seen any exceptions Ron
ritelec Senior Member Location Jersey Feb 6, 2020 #4 olk thank you. The directions do say NEVER hang this unit on wall directly below an electrical outlet. So there it is. Ok. What if the recpt was 10 or 20 feet above ???? Or on the next floor above :- ) Kidding. Is what it is. Ty
olk thank you. The directions do say NEVER hang this unit on wall directly below an electrical outlet. So there it is. Ok. What if the recpt was 10 or 20 feet above ???? Or on the next floor above :- ) Kidding. Is what it is. Ty
ritelec Senior Member Location Jersey Feb 6, 2020 #5 Heater people. Two wire cord plug feeding it 1500 w. 12.5 amps. It says use heater on 15 amp circuit. Have I just violated by putting on s 20 amp Do these directions supersede the 80 percent on a 15 amp circuit ? Unit is 12.5?
Heater people. Two wire cord plug feeding it 1500 w. 12.5 amps. It says use heater on 15 amp circuit. Have I just violated by putting on s 20 amp Do these directions supersede the 80 percent on a 15 amp circuit ? Unit is 12.5?
E Eddie702 Licensed Electrician Location Western Massachusetts Occupation Electrician Feb 6, 2020 #6 I think I would put it on a 15 if it's listed that way. Safe thing is to run #12 with a 15 so you could change it to a 20 later if need be.
I think I would put it on a 15 if it's listed that way. Safe thing is to run #12 with a 15 so you could change it to a 20 later if need be.