I am working as a consultant at a manufacturing plant in CA. The facility has 208V receptacle panels in hallways and areas accessible by anyone in the company (500 people).
The Maintenance Manager took a OSHA class years ago that stated the panels should be kept locked unless they are located in a room with controlled access - Mechanical or Electrical room for instance.
I agree with this practice, but have been asked for a code requirement to back it up. Others question the need for this and prefer to have them unlocked for convenience.
NFPA 70E section 130.6.M states that "After a circuit has been de-energized by the automatic operation of a circuit protective device, the circuit shall not be manually re-energized until it has been determined that the equipment and circuit can be safely energized".
I can interpret that to mean only Qualified Persons can make this determination and therefore all others should not be allowed access to the protective device.
There is a company Electrical Safety Program in place, but there is no mention of access to breakers.
There are also 480V Distribution Panels in common areas that are not lockable - the breakers are mounted on the front with no door to lock. If the 208V panels need to be locked, what about those?
I appreciate your feedback and expertise.
The Maintenance Manager took a OSHA class years ago that stated the panels should be kept locked unless they are located in a room with controlled access - Mechanical or Electrical room for instance.
I agree with this practice, but have been asked for a code requirement to back it up. Others question the need for this and prefer to have them unlocked for convenience.
NFPA 70E section 130.6.M states that "After a circuit has been de-energized by the automatic operation of a circuit protective device, the circuit shall not be manually re-energized until it has been determined that the equipment and circuit can be safely energized".
I can interpret that to mean only Qualified Persons can make this determination and therefore all others should not be allowed access to the protective device.
There is a company Electrical Safety Program in place, but there is no mention of access to breakers.
There are also 480V Distribution Panels in common areas that are not lockable - the breakers are mounted on the front with no door to lock. If the 208V panels need to be locked, what about those?
I appreciate your feedback and expertise.