Receptacle placement in Office building

Status
Not open for further replies.

Designer69

Senior Member
The NEC has requirements for dwelling units, what about an office building any special requirements there or place them where you please?


Thanks
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
For a dwelling unit, the recp loads are included in the 3VA/SQ F calulation. For an office building, each recp is counted at 180VA. There are only a few non dwelling unit recpts required, one that comes to mind is for the service area.
 