D Designer69 Senior Member Mar 17, 2019 #1 The NEC has requirements for dwelling units, what about an office building any special requirements there or place them where you please? Thanks
The NEC has requirements for dwelling units, what about an office building any special requirements there or place them where you please? Thanks
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Mar 17, 2019 #2 For a dwelling unit, the recp loads are included in the 3VA/SQ F calulation. For an office building, each recp is counted at 180VA. There are only a few non dwelling unit recpts required, one that comes to mind is for the service area.
For a dwelling unit, the recp loads are included in the 3VA/SQ F calulation. For an office building, each recp is counted at 180VA. There are only a few non dwelling unit recpts required, one that comes to mind is for the service area.
P packersparky Senior Member Location Wisconsin Occupation Inspector Mar 17, 2019 #3 210.71 if you are on the 2017 NEC and the office building has meeting rooms.
kwired Electron manager Location NE Nebraska Occupation EC Mar 18, 2019 #4 packersparky said: 210.71 if you are on the 2017 NEC and the office building has meeting rooms. Click to expand... That plus there is also 210.62, .63 and .64 that may apply.
packersparky said: 210.71 if you are on the 2017 NEC and the office building has meeting rooms. Click to expand... That plus there is also 210.62, .63 and .64 that may apply.