Is this what you are looking for? There are a few exceptions

406.12 Tamper-Resistant Receptacles. All 15- and 20-ampere,
125- and 250-volt nonlocking-type receptacles in the areas
specified in 406.12(1) through (7) shall be listed tamperresistant
receptacles.
(1) Dwelling units in all areas specified in 210.52 and 550.13
(2) Guest rooms and guest suites of hotels and motels
(3) Child care facilities
(4) Preschools and elementary education facilities
(5) Business offices, corridors, waiting rooms and the like in
clinics, medical and dental offices and outpatient facilities
(6) Subset of assembly occupancies described in 518.2 to
include places of waiting transportation, gymnasiums,
skating rinks, and auditoriums
(7) Dormitories
 
Along with Dennis's post there is Part III of article 210.

Roger
 
There are almost no requirements for receptacles for non-dwelling occupancies. It is left to the designer for the most part.
 
As Don mentioned, the NEC for non dwelling locations only has a few receptacle req: Electrical service area, HVAC, conference rooms. Now those recepts, where installed may need to be GFCI.
 