Shouldn't it be permissible to install a 15 amp duplex receptacle on a dedicated 20 amp circuit for a microhood, as long as the appliance draws less than 12 amps?
Actually a simplex would also be compliant. 210.19(B)(3) says "Where connected to a branch circuit supplying two or more receptacles or outlets, ..."15 amp duplex receptacle, yes. 15 amp simplex receptacle, no.
Ahh! A most important distinction....
But not OK to install a single simplex receptacle into which you will plug the microhood.
Two outlets IF you interpret the OP's question to be about adding a new simplex receptacle in addition to a hard wired microhood, .
Sent from my XT1585 using Tapatalk
If you connect another outlet (the receptacle) the circuit is no longer dedicated, i.e. not an individual branch circuit.But you could not plug anything into the receptacle.
OP said dedicated circuit by which I infer he meant individual.
Branch Circuit, Individual. A branch circuit that supplies
only one utilization equipment.
If you connect another outlet (the receptacle) the circuit is no longer dedicated, i.e. not an individual branch circuit.
I'm not saying it is... but as soon as you plug in something, the branch circuit is supplying two pieces of utilization equipment. It cannot be an individual branch circuit.AFAICT a plain receptacle is not another piece of utilization equipment........
Utilization Equipment. Equipment that utilizes electric
energy for electronic, electromechanical, chemical, heating,
lighting, or similar purposes.
So, to sum it up, the additional receptacle is OK, you just are not allowed to plug anything into it ever.I'm not saying it is... but as soon as you plug in something, the branch circuit is supplying two pieces of utilization equipment. It cannot be an individual branch circuit.
I'm not saying it is... but as soon as you plug in something, the branch circuit is supplying two pieces of utilization equipment. It cannot be an individual branch circuit.
I'm well aware of the definition... and what I'm saying is when you add a second outlet to an individual branch circuit... it is no longer an individual branch circuit. It's not rocket science.See post #6.![]()
IOW, by using a duplex receptacle - you now have 2 outlets and it is no longer a Branch circuit, IndividualI'm well aware of the definition... and what I'm saying is when you add a second outlet to an individual branch circuit... it is no longer an individual branch circuit. It's not rocket science.
I'm well aware of the definition... and what I'm saying is when you add a second outlet to an individual branch circuit... it is no longer an individual branch circuit. It's not rocket science.
I would like to hear from the OP. I don't see where you get the impression he was installing an additional outlet or your distinction of two outlets for the microhood. In fact, I think it is a stretch to interpret it that way. He says "dedicated" it is a much more likely interpretation that he is installing a circuit and a receptacle for a microhood. Not extending an existing one, thereby adding a receptacle. A few months ago we were chastised for overcomplicating our answers and I argued that complexity is one of the benefits of the site, but this answer is definitely what iWire was referring to.
If it needed a 20 amp receptacle they would have put a 20 amp cord cap on it IMO.For clarification I am installing a individual 20 amp circuit to a box in the cabinet above the microhood and installing a standard 15 amp duplex receptacle. The microwave plugs in to one of the receptacles on that duplex leaving one other receptacle unused. It is just one device, not two separate devices. The inspector is saying I can't do that because it says on the microwave that the circuit input is 1800 watts. But it also says the output is only 1100 watts. He is claiming I have to go by the input and not the output of the appliance. It doesn't say in the instructions that is has to be on a individual circuit either. The inspector doesn't care that it is a duplex receptacle, he just wants it to be a 20 amp rated receptacle.
If it needed a 20 amp receptacle they would have put a 20 amp cord cap on it IMO.
That 1100 output watts is likely the microwave output, you also ordinarily have a range hood fan and light(s), though they are not normally going to be 700 watts - the difference is all inefficiency.
I agree your first reply was correct, there just may have been more to the question then the words presented.Agreed. And for your comment on my post. I answered him correctly for the question he was asking in my first post.
My bad for going the outlet direction. I read the OP as a hardwired microhood and the receptacle being in addition to.I would like to hear from the OP. I don't see where you get the impression he was installing an additional outlet or your distinction of two outlets for the microhood. In fact, I think it is a stretch to interpret it that way. He says "dedicated" it is a much more likely interpretation that he is installing a circuit and a receptacle for a microhood. Not extending an existing one, thereby adding a receptacle. A few months ago we were chastised for overcomplicating our answers and I argued that complexity is one of the benefits of the site, but this answer is definitely what iWire was referring to.