(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit.
A single receptacle installed on an individual branch circuit
shall have an ampere rating not less than that of the branch
circuit.
An appliance cut sheet says it requires a dedicated 15 Amp dedicated outlet. Is a 15 A simplex receptacle required or can a 15 A duplex receptacle be used knowing that only this one appliance will be plugged into it?
Neither the phrase "dedicated outlet" nor the phrase "dedicated circuit" appears in the NEC. I think you can install a duplex for this application.
Really Dennis --Outlet.
A point on the wiring system at which current is
taken to supply utilization equipment. - time to look up dedicated since it is not in the code -- Dedicated 15A outlet = dedicated 15a branch circuit to serve the equipment - the OP wanted the meaning of the manufactures requirement -- outlet & receptacle are two different definitions
The only thing I can think of is a 15 ampere circuit limits the max load of the cord and plug load to 12 A, so while the unit draws 10 A that leaves a maximum of 2 A load allowed if someone plugs something else in to another receptacle if a duplex is used. Also, since the wording in the cut sheet says 15 A dedicated outlet, doesn't that mean a simplex is required because of the word dedicated?