Re: Receptacle Rating
The NEC is comprised mostly of ?This is OK? kinds of statements, with a smaller percentage of the text comprising ?This is not OK? kinds of statements. The game rules for using the NEC include this one:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">?If it does not say that ?This is not OK,' then it is OK.?</font>
<font size="2" face="Verdana, Helvetica, sans-serif">Article 210.21(B) falls under 210, ?Branch Circuits,? Part II, ?Branch-Circuit Ratings.? Nothing in either of those two titles restricts the discussion to, or away from, any specific type of branch circuit. In other words,
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">This article DOES say that putting 2 or more 15 amp receptacles on a 20 amp circuit is OK</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">This article DOES NOT say that putting 2 or more 15 amp receptacles on a 20 amp Small Appliance or Laundry circuit is not OK</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Therefore, we may conclude that putting 2 or more 15 amp receptacles on a 20 amp Small Appliance or Laundry circuit IS OK</font>
<font size="2" face="Verdana, Helvetica, sans-serif">Will that perspective be enough to convince the other half of your discussion group?