Receptacle Rating
2SIN54
Hi and thanks for the opportunity to use this incredible resource!
BTW, I do have the 2011 NEC code book.
Just had a question regarding receptacle ratings. I have watched Mike Holt's video on 15-ampere & 20-ampere rated receptacles being the same internally and the only difference being the face plate etc. Thus, 15-ampere duplex receptacles are allowed to be used on a 20-ampere branch circuits NEC 210.21(B)(3).
Then, in 210.21(B)(1) it says that a "single" receptacle used on an individual branch circuit shall have an ampere rating not less than that of the branch circuit. FYI, I'm disregarding the exceptions there.
So, my question(s) are ~
{A} Per mike's video on the dual rating of 15-ampere rated duplex receptacles, can it be found in writing this is a fact. I agree that this is the case and understand the engineering behind it, I just wondered how to definitively indicate this to someone else who would question the matter.
{B} Does a 15-ampere rated "single" receptacle carry the same dual rating?
{C} Would it be permissible to use two or more 15-ampere rated "single" receptacles on a 20-ampere rated branch circuit?
Thanks
(A) The receptacle specification will indicate that it's 20 amp feed through which I would guess is part of the listing of the 15 amp duplex.
(B) I would say no (but it could be) since a single receptacle has only one screw terminal for each conductor and is not used as a feed through.
(C) Yes, also a single duplex is considered two receptacles.
Yea from what I can find the single's do not indicate a dual rating as most duplexes do. Last time I really dealt with single's was in an older nursing home for AC/heat units in each room, I think we updated them to 20's where they needed replaced.
Actual feed thru ratings really only matters when feeding thru.
NEC specifically allows 15 amp receptacles on 20 amp circuits if it is a multi-outlet circuit. One duplex receptacle fulfills that multi-outlet term.