Hi and thanks for the opportunity to use this incredible resource!
BTW, I do have the 2011 NEC code book.
Just had a question regarding receptacle ratings. I have watched Mike Holt's video on 15-ampere & 20-ampere rated receptacles being the same internally and the only difference being the face plate etc. Thus, 15-ampere duplex receptacles are allowed to be used on a 20-ampere branch circuits NEC 210.21(B)(3).
Then, in 210.21(B)(1) it says that a "single" receptacle used on an individual branch circuit shall have an ampere rating not less than that of the branch circuit. FYI, I'm disregarding the exceptions there.
So, my question(s) are ~
{A} Per mike's video on the dual rating of 15-ampere rated duplex receptacles, can it be found in writing this is a fact. I agree that this is the case and understand the engineering behind it, I just wondered how to definitively indicate this to someone else who would question the matter.
{B} Does a 15-ampere rated "single" receptacle carry the same dual rating?
{C} Would it be permissible to use two or more 15-ampere rated "single" receptacles on a 20-ampere rated branch circuit?
Thanks
BTW, I do have the 2011 NEC code book.
Just had a question regarding receptacle ratings. I have watched Mike Holt's video on 15-ampere & 20-ampere rated receptacles being the same internally and the only difference being the face plate etc. Thus, 15-ampere duplex receptacles are allowed to be used on a 20-ampere branch circuits NEC 210.21(B)(3).
Then, in 210.21(B)(1) it says that a "single" receptacle used on an individual branch circuit shall have an ampere rating not less than that of the branch circuit. FYI, I'm disregarding the exceptions there.
So, my question(s) are ~
{A} Per mike's video on the dual rating of 15-ampere rated duplex receptacles, can it be found in writing this is a fact. I agree that this is the case and understand the engineering behind it, I just wondered how to definitively indicate this to someone else who would question the matter.
{B} Does a 15-ampere rated "single" receptacle carry the same dual rating?
{C} Would it be permissible to use two or more 15-ampere rated "single" receptacles on a 20-ampere rated branch circuit?
Thanks