Receptacle required <25' from a thru the wall hvac unit?

Status
Not open for further replies.
Here's what the NEC requires:

210.63 Heating, Air-Conditioning, and Refrigeration Equipment Outlet.
A 125-volt, single-phase, 15- or 20-ampere-rated receptacle outlet shall be installed at an accessible location for the servicing of heating, air-conditioning, and refrigeration equipment. The receptacle shall be located on the same level and within 7.5 m (25 ft) of the heating, air-conditioning, and refrigeration equipment. The receptacle outlet shall not be connected to the load side of the equipment disconnecting means.
Exception: A receptacle outlet shall not be required at one- and two-family dwellings for the service of evaporative coolers.

Does your unit fit the description?
 