My own guidelines:
If there are two cables in the box, I only pigtail the ground, using the receptacle to pass thru. AFCI and GFCI receptacles are rarely pigtailed unless I just need protection at that one receptacle.
If there are three or more cables, I pigtail everything rather than using the backstabs on the device.
Istm that most commercially trained electricians pigtail everything and resi sparkies just the ground. Not pigtailing is a bit faster and there's less actual* box fill since there are two less wagos/wirenuts. Calculated box fill is the same either way.
If there are two+ receptacles/switches in the box, I tail to all rather than using one wire looped around a screw on each device.
I do the same here! good practice I think
So if any one of those wires comes out of the back of the receptacle then you lose all other receptacles Downstream of it. Seems like an easy way of getting out of pigtailing, just so you can do it faster.
Sent from my Moto G (4) using Tapatalk
The post you quoted and the other that was related to it didn't say they "back stabbed"