on a single receptacle installation on a individual branch circuit what ampere rating are required, less to most
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: receptacle

Is this home work?

Not that it is all inclusive, but what you're probably looking for is in article 210.

Roger

[ October 30, 2003, 08:16 PM: Message edited by: roger ]
 

big john

Senior Member
Location
Portland, ME
Re: receptacle

Not really sure what you're asking, so here's my best shot.

210.21(B)(1)
A single receptacle on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.

406.2(B)
Receptacles and cord connectors shall not be rated for not less than 15 amps, 125 volts, or 15 amps 250 volts....

-John
 

dianes

Member
Re: receptacle

on a single receptacle installed on an individual branch circuit shall have an ampere rating of not less than what percent of the rating of a branch circuit.
 

charlie

Senior Member
Location
Indianapolis
Re: receptacle

Dianes, Roger asked you if this was homework and you did not answer. It looks like homework to me and the question has been answered. I am locking this thread.
 