Receptacles above drop cieling?

Status
Not open for further replies.

dedshort

New member
Location
omaha nebraska
I have noticed a few threads on here concerning this, I have a question about a situation that I am running into right now. I have read 400.7-400.8 (5)
My question is, I have a request to place a receptacle above ceiling for a plug in low volt transformer for security camera's, the transformer screws in to the receptacle to prevent removal accidentally. My question is, this is not a cord that takes 120 that is going to be strung across the ceiling above the pads, so being LV plenum rated cabling, is this acceptable?
 
My question is, this is not a cord that takes 120 that is going to be strung across the ceiling above the pads, so being LV plenum rated cabling, is this acceptable?
Your installation is fine.

Roger
 
I agree also. Receptacles are permitted above the ceiling but flexible cords are not. Since you transformer is plugged into the receptacle you are OK.
 