The receptacle above the ceiling is compliant but 400.8(5) does not permit a flexible cord to be installed. they would be service outles
400.8 Uses Not Permitted. Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following:
- As a substitute for the fixed wiring of a structure
- Where run through holes in walls, structural ceilings, suspended ceilings, dropped ceilings, or floors
- Where run through doorways, windows, or similar openings
- Where attached to building surfaces Exception to (4): Flexible cord and cable shall be permitted to be attached to building surfaces in accordance with the provisions of 368.56(B)
- Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings
- Where installed in raceways, except as otherwise permitted in this Code
- Where subject to physical damage