Receptacles for servicing conveyor motors

Status
Not open for further replies.

JDBrown

Senior Member
Location
California
Occupation
Electrical Engineer
I'm reviewing a design for a baggage screening system, and I've noticed a lack of convenience receptacles near the conveyor motors. My supervisor tells me that the NEC requires a receptacle to be installed within x number of feet of each motor, but I can't find such a requirement anywhere. I'm familiar with 210.63, but that only applies to Heating, Air Conditioning, and Refrigeration equipment.

Is there a Code section similar to 210.63 that requires a receptacle to be installed near all motors? In the case of the plans I'm reviewing, I think the designer should add them for ease of future servicing, but I need to know if it's a Code requirement.
 
Given the prevalence of battery powered tools and work lights, I am not sure what use the convenience outlet would be in your situation.
For HVAC the service tech may need to operate a refrigerant scavenging pump, which is hard to find with battery power.

Tapatalk!
 
Is there a Code section similar to 210.63 that requires a receptacle to be installed near all motors? In the case of the plans I'm reviewing, I think the designer should add them for ease of future servicing, but I need to know if it's a Code requirement.
No such requirement. The section you cited is as close as you will get.
 
Thanks for the replies, guys. That's what I figured, but I wanted to get some confirmation before telling the boss he's wrong. :)