I am quoting a job and this is it.
install 120v receptacle in the top portion of lockers for guys to be able to charge cell phones, charge electric shavers, etc in a locker room. (100 lockers). The top portion of these lockers have a locking door so the receptacle would be mounted in the back of the top locker portion.
Commercial building, all lockers are at least 10ft from any water source so i don't think any GFI protection is required.
I plan on putting 13 duplex receptacles on each 20amp circuit per 220.14 (I).
Does anything ring a bell for any requirements i may not be thinking of regarding this installation?
thanks for your input.
install 120v receptacle in the top portion of lockers for guys to be able to charge cell phones, charge electric shavers, etc in a locker room. (100 lockers). The top portion of these lockers have a locking door so the receptacle would be mounted in the back of the top locker portion.
Commercial building, all lockers are at least 10ft from any water source so i don't think any GFI protection is required.
I plan on putting 13 duplex receptacles on each 20amp circuit per 220.14 (I).
Does anything ring a bell for any requirements i may not be thinking of regarding this installation?
thanks for your input.