I have a kitchen where 2 of 3 sides would be considered peninsulas. ( plus an island ). There is no back wall on one of the 2 peninsulas, and nothing goes higher than the counter. I am looking for a NARROW pop up for one wall ( 3.5" metal stud ) and a low/minimal space pop-up for the other wall at a reasonable price...
Any suggestions would be appreciated...see attached...Thanx..dhsvcs
 

Attachments

  • overall view.pdf
    36.5 KB · Views: 2
  • Section A.jpg
    Section A.jpg
    33.3 KB · Views: 12
  • Section B.jpg
    Section B.jpg
    31.2 KB · Views: 11
  • View1.jpg
    View1.jpg
    48.8 KB · Views: 11
  • View2.jpg
    View2.jpg
    19.9 KB · Views: 13
  • overall view 1.jpg
    overall view 1.jpg
    230.1 KB · Views: 12

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I assumed 2017
Section A will need a receptacle probably at the far right within 12" of the top
Section B, I believe, will only need the one on the wall but that doesn't look possible so one at the end of the peninsula would work.
The island will need one
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
WC was quite a character

I assumed that the island had 12" behind the cooktop which would make the island require only one receptacle

(4) Separate Spaces. Countertop spaces separated by rangetops,
refrigerators, or sinks shall be considered as separate
countertop spaces in applying the requirements of
210.52(C)(1). If a range, counter-mounted cooking unit, or
sink is installed in an island or peninsular countertop and the
depth of the countertop behind the range, counter-mounted
cooking unit, or sink is less than 300 mm (12 in.), the range,
counter-mounted cooking unit, or sink shall be considered to
divide the countertop space into two separate countertop
spaces. Each separate countertop space shall comply with the
applicable requirements in 210.52(C).
 

dhsvcs

Member
Location
miami
Occupation
electrician
There are no side walls...gets a little tricky..
I will try to give the customer a couple of recepts per side, bit pop-ups and flip ups becomes expensive.
I am thinking on the opposite side of the counters I may place one and I will need to check clearance for drawers...
 

Attachments

  • Rev 3.jpg
    Rev 3.jpg
    224.7 KB · Views: 3

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
One peninsula butts into a wall below a window. The receptacle can go there. I always worked with the cabinet guys to make sure their was room for the required outlets or for what the owners wanted.
 