Similar questions have been asked in the past on this forum, but are slightly different than my question, and they are possibly outdated. This question pertains to NEC 2011.
We are connecting motorized shades in classrooms to power. Each shade comes with a local power supply that connects to power via a receptacle and plug/cord connection. Each classroom has a drop ceiling that is being used as a plenum. Two questions:
1.) Can I install a duplex receptacle above the drop ceiling for the motorized shades? I don't see anything in article 300.22 that precludes this.
2.) In most cases, according to article 400.8, using a flexible cord above a drop ceiling is not permitted. However, would flexible cords be allowed for motorized shades as per 400.7(A)(9), i.e. because the shades are considered "connection of moving parts"?