That works in "general terms" if you keep in mind that calculation is for "other outlets" listed in 220.14. There are many instances where that "formula" does not apply such as specific loads, multi-out assemblies, etc. You need to review 220.14 before applying.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
To determine how many on a circuit is the calculation = VoltsxOCPD Amps then divide that by 180va? Thanks.

If this is a dwelling you would use the 3va/Sq ft calculation to find the minimum number of circuits. How many you put on a circuit is not limited by your calculation.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
120V x 20A x .80 = 1920VA divide by 180

Unless specific loads are known for specific recepts
i must also ask why the 80%? There is no need to figure general receptacle circuits for continuous loading.