Perhaps the reason is that the code making panels could not justify forcing all circuits to be GFCI protected. It's not impossible that things will evolve that way, but it's not likely to happen quickly.Originally posted by dpenbert: Can you explain why not?
Under the 2005 code, it is possible that you would have to provide GFCI protection. The change in the 2005 code requires that all 125 volt, 15 or 20 amp recpetacles installed within 6' of the outside edge of a laundry sink. There are no exceptions.Is it required that the washer and dryer circuits be GFCI protected?
And that's a good thing! After all, when I pick up the washer with one hand, so that I can sweep the floor under it with the other hand, I might accidentally drop it into the laundry sink.Originally posted by don_resqcapt19: The change in the 2005 code requires that all 125 volt, 15 or 20 amp receptacles installed within 6' of the outside edge of a laundry sink. There are no exceptions.