Receptacles per circuit

Status
Not open for further replies.

tmacdonald

Member
Location
Saginaw, MI
How many 120V receptacles can you put on a 20A branch circuit?

I'm working on a healthcare project and I'm using 180VA for general power receptacles. I see an example in the '99 handbook that shows 13 (2340VA). I though we could not load a circuit beyond 80%.
 

hornetd

Senior Member
Location
Maryland
Occupation
Journeyman Electrician, Retired
Re: Receptacles per circuit

The 80% figure aplies to continuous loads only. The convenience receptacles are not considered continuous loads.
--