Ive heard that there is a code that says receptacles are supposed to stick out from the cover plate a certain amount does anybody know where this is at in the code book?
I remember flush with plastic plates and protruding with metal for some reason.
406.4(D) Position of Receptacle Faces. After installation, receptacle faces shall be flush with or project from faceplates of insulating material and shall project a minimum of 0.4 mm (0.015 in.) from metal faceplates.
Exception: Listed kits or assemblies encompassing receptacles and nonmetallic faceplates that cover the receptacle face, where the plate cannot be installed on any other receptacle, shall be permitted.
That'll do it.Probably because of this;
Why is that, anyway?
Obviously, to minimize sparks.Why is that, anyway?