This is not a requirment of the NEC unless the manufacture requires it. See the FPN of 210.52

210.52 Dwelling Unit Receptacle Outlets.
This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. Receptacle outlets required by this section shall be in addition to any receptacle that is part of a luminaire (lighting fixture) or appliance, located within cabinets or cupboards, or located more than 1.7 m (5? ft) above the floor.
Permanently installed electric baseboard heaters equipped with factory-installed receptacle outlets or outlets provided as a separate assembly by the manufacturer shall be permitted as the required outlet or outlets for the wall space utilized by such permanently installed heaters. Such receptacle outlets shall not be connected to the heater circuits.

FPN: Listed baseboard heaters include instructions that may not permit their installation below receptacle outlets.
 

charlie

Senior Member
Location
Indianapolis
Re: Recepticals above baseboard heater

IMHO, using a person's e-mail address to post an answer directly to him will deprive everyone else of the information which is what this forum is about. I hope people do not respond to individual requests for information and just use e-mail addresses for sending personal correspondence. :cool:
 

hurk27

Senior Member
Re: Recepticals above baseboard heater

Me too as even when I get a PM I will still post the responce in the forum for all to see I have nothing to hide LOL.
speechless-smiley-039.gif
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: Recepticals above baseboard heater

2002 NEC 110.3 Examination, Identification, Installation, and Use of Equipment.
(A)(5) Heating effects under normal conditions of use and also under abnormal conditions likely to arise in service.
(A)(8)Other factors that contribute to the practical safeguarding of persons using or likely to come in contact with the equipment

(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
 

lady sparks lover

Senior Member
Re: Recepticals above baseboard heater

Originally posted by frankiedynomite:
I am uncertain of the code that pertains to electrical recepticals located above a heating element. If someone could e-mail me with the correct information I would really appreciate it, thanks. frankiedynamo@yahoo.com
i have no comment, i just like the your name... :)
 
B

bthielen

Guest
Re: Recepticals above baseboard heater

I wonder if an appliance cord would be subjected to excessive ambient temperature were it plugged into a receptacle just above a baseboard heater or other heat source such as a stovetop. Is there a responsibility to consider this when wiring a home or only to meet the requirements of the code up to the receptacle?

Bob
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Re: Recepticals above baseboard heater

210 Part II: Required Outlets

nec 210.52 Dwelling Unit Receptacle Outlets.

FPN: Listed baseboard heaters may include instructions that may not permit their installation below receptacle outlets.

210.52(A) General Provisions: In every kitchen, family room, dining room, living room, parlor, library, den, sunroom, bedroom, recreation room, or similar room or area of dewlling units, receptacle outlets shall be installed in accordance with the general provisions specified in 201.52 (A)(1) through (3).

(1) Spacing: Receptacles shall be installed so that no point measured horizontally along the floor line in any wall space is more than 6 ft. from a receptacle outlet.

Steve
 

charlie

Senior Member
Location
Indianapolis
Re: Recepticals above baseboard heater

The listing has the following from the 2003 UL White Book, the bolding is mine:

Electrical cords, drapes, and other furnishings should be kept away from baseboard heaters. To reduce the likelihood of cords contacting the heater, the heater is not to be located beneath electrical receptacles. Listings of receptacle accessories for use with an individual manufacturer's baseboard heaters are included under the category "Baseboard Heater Accessories" (KLQZ).

Since these are the listing requirements, take a look at websparky's post. :D
 