Daniel Noblet
New member
Had a discussion with a guy tonight that ended as most do with him. He doesn't care. Replaced two wire recept. with three wire (grounding type) recepticles and I asked him if he knew why it was a code violation to do that.
You give a false sence of sucurity it is a three wire recept. with a grounding conductor attached. It'll be fine, nothing will ever happen. Maybe not.
To my understanding replacement must be done with 2 pole recept. or a GFCI recept. indicating there is no grounding conductor supplied at this recept.
He told me he took a pigtail wire from the grounded conductor and attached it to the grounding conductor terminal. That's good enough it's attached to the ground and it will fool those pesky little recept. testers.
I really don't think he understands the differance between a
grounded conductor and a grounding conductor.
Would someone with more knowledge than I explain the hazzards of this. I made the mistake of telling him any jackass can put a couple of wires together and make a light work but it doesn't make it safe and legal.
You give a false sence of sucurity it is a three wire recept. with a grounding conductor attached. It'll be fine, nothing will ever happen. Maybe not.
To my understanding replacement must be done with 2 pole recept. or a GFCI recept. indicating there is no grounding conductor supplied at this recept.
He told me he took a pigtail wire from the grounded conductor and attached it to the grounding conductor terminal. That's good enough it's attached to the ground and it will fool those pesky little recept. testers.
I really don't think he understands the differance between a
grounded conductor and a grounding conductor.
Would someone with more knowledge than I explain the hazzards of this. I made the mistake of telling him any jackass can put a couple of wires together and make a light work but it doesn't make it safe and legal.