360Youth
Senior Member
- Location
- Newport, NC
Today was a new one for me and I was wondering if anybody has had the same problem. We are trimming out a home right now and when I turned on a set of cans the other day, the breaker blew. I climbed into the attic to check out the j-boxes and everything looked good. I remembered some weird popping on some of the other cans when the switch was turned on but it was a split second one time deal with no lamp or breaker issues, so I chalked it up to excess paint on the shell and started double checking them as we put the lamps in. So anyway, because of that, on these that that were tripping the breaker, I decided to unlamp them and try the switch again. Everything was good. I got my ladder and a flashlight and sure enough, inside the socket, the tab was pushed back and shorting against the can. I had to fabricate a tiny hook to get behind the tab and pull it down on all five cans. I relamped and everything was good. We have about 50 more up and running so far and have not had the same problem, nor can I ever remember shorting out a recessed can by screwing in the lamp too far. Anybody else have that problem before?