Recessed Lights J Boxes
kgettrost
Would a J-box that is part of a recessed light for installation in a SFH need protection on the end factory knockout? In Article 314 [Construction Specifications] 314.40 Metal Boxes,Conduit Bodies, & Fittings. Section 314.42 Bushings.Openings shall be provided with approved bushings or shall have smooth, well-rounded surfaces on which the cord may bear. Also in the box is a cable-grip is this enough to secure cable to the box? This is not a clamp but only a piece of spring steel. Per the juno recessed light IC & TC. The contractor thinks because of this listing no protection is needed for the knockouts, or nothing else is need to secure the cable.
raider1
Logan, Utah
314.42 applys to covers of outlet boxes throught which flexible cord pendants may pass. This section would not apply to a J-box attached to a listed recessed can.
Chris
buckle40
I would agree that this would be true if you were trying to use article 314 for pendent. However, if you go to article 300 section 300.4 B 1 it is required.
raider1
Logan, Utah
300.4(B)(1) deals with NM cable running through metal framing members (metal studs). This section does not address NM cable entering an electrical box.
Chris
raider1
Logan, Utah
And what about 314.17 B
314.17(B) applys to messenger supported wiring, open wiring on insulators, or concealed knob and tube wiring, not to NM cable.
The factory supplied cable clamp and opening in a Juno can IMHO is fine without additional protection. I don't see these opening any different than the factory openings with cable clamps in 4sq or 4/0 boxes that are designed for NM cable.
Chris
LJSMITH1
Stratford, CT
When in doubt, consult the Manufacturer's installation instructions. If it is a standard j/b design with a std. knockout, more than likely you would need an applicable connector to secure the cable to the box (NM or AC/MC). The only time that this would not apply, if if the j/b has a built in cable/conduit clamp that requires no fitting. However, the clamp will typically be stamped for use with either MC/AC or NM.
celtic
NJ
The last line of 314.17(B) would seem to be written that it DOES apply to NM:
Where raceway or cable is installed
with metal boxes or conduit bodies, the raceway or
cable shall be secured to such boxes and conduit bodies
410.56(A) & (B) seems address this "issue" as well.
EDIT:
I agree
buckle40
If this so why does the manufacture tell you to check with local building department concerning the contains in the j-box.
buckle40
If this so why does the manufacture tell you to check with local building department concerning the contains at the j-box. Moreover, the contactor but the cables thru a knock only with no connector. And that this was ok per the listing.:-?
celtic
NJ
For the same reason cigarettes have a warning label on them ~ liability.
The manufac. has no idea what code cycle a given area is under, the "Get out of jail free card" is to have the installer check with the local AHJ.
I don't understand what you have written :-?
LJSMITH1
Stratford, CT
Juno Type IC and Type TC housings state the following in the installation instructions:
Step 2. Remove wiring box cover. Remove
the appropriate knock-out(s)
to accommodate the type of electrical service
to be used/allowed by your local electrical
code (Fig. 9):
Metal Conduit. Remove appropriate round
knock-out(s) and connect conduit to wiring
box with proper connectors (not supplied.)
Non-Metallic Cable. Remove appropriate
knock-out(s) from top of wiring box and
insert cable, pushing it past the cable grip.
No other connector is required.
celtic
NJ
Halo has the same:
Step 2
Remove the wiring box cover.
Remove the appropriate knock-out(s) to accommodate the type of electrical service to be used.
Note: The wiring box will accept metal conduit or non-metallic cable, but metal conduit must be used if your electrical code requires it.
Metal Conduit: Remove appropriate round knock-out(s) and connect conduit to wiring box with proper connector(s) (not included).
Non-metallic Cable: Remove appropriate rectangular knockout( s) on top of wiring box and insert cable, pushing it past the cable lock in wiring box. Cable will be held in place by the lock; no other connector is required (Fig 4).
[NOTE: Fig. 4 is basically the photos I show above]
H99ICT
If one chooses to use the standard 1/2" KOs ~ a proper connector MUST be used ~ you cannot just slip the NM through the 1/2" KO.