Recessed MR16 in a closet space

Status
Not open for further replies.

cbishop7

Member
Tried searching the forum, but no luck.

Can you install a recessed MR16 in a closet space? I imagine is should be covered/lensed.

NEC section 410.16 doesn't address low voltage fixtures one way or another as allowed or not allowed.

Thoughts??
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Tried searching the forum, but no luck.

Can you install a recessed MR16 in a closet space? I imagine is should be covered/lensed.

NEC section 410.16 doesn't address low voltage fixtures one way or another as allowed or not allowed.

Thoughts??

Here's the code wording. The lamp needs to be completely enclosed, whatever that means.

410.16 Luminaires in Clothes Closets.
(A) Luminaire Types Permitted. Listed luminaires of the following types shall be permitted to be installed in a closet:
(1) A surface-mounted or recessed incandescent luminaire with a completely enclosed lamp
(2) A surface-mounted or recessed fluorescent luminaire
(3) Surface-mounted fluorescent or LED luminaires identified as suitable for installation within the storage area
(B) Luminaire Types Not Permitted. Incandescent luminaires with open or partially enclosed lamps and pendant luminaires or lampholders shall not be permitted.
 