Recommend a dropping transformer
cudco
CT
Engineer
From your experience, would any one of you experts be able to recommend a reliable dropping transformer brand capable of:
3-phase, 60Hz
480V primary
400V secondary
40kVA min.
Thanks!
Yes, we are, but wanted some recommended brands from other people's experience.
For 400V 'Nominal Utilization Voltage', such as 400V 60HZ nameplate motors I use a 416Y/240 "Nominal System Voltage". So you'll want to search for a 480 D : 416Y/240 transformer.
Maddox makes one
All the major manufacturers are starting to support 416V.
Thank you, did not know about 416V (weird supply), so looking into it I found the following:
States that 416V is primarily for Crypto-Mining application.
We're looking for European equipment to come into the US that requires 400V, so most likely will stick with 400V secondary.
Is Maddox reputable?
Don't believe everything technical you read on the internet.
People have been using 416/240V system for decades. They power European equipment as well as computer power supplies. The problem with European equipment is it often wants 50Hz.
I have installed several Maddox transformers in the past couple years, haven’t had an issue yet. They are very quiet.
Thanks for the comment. I'll have to review with others here.
433Y/250 V or 416Y/240 V is super normal in data centers. The most economic setup is one where a double conversion online UPS accepts standard 480 V utility service and outputs 240 V.
Have purchased a few HPS (Hammond) transformers over the years.
Here is a screenshot of some standard 3 phase (aluminum winding) step down units from their catalog ...
When you to the bottom, dry-type transformers are quite reliable and most (all) on the market will be UL listed. The chief selectors are usually what the local supplier carries or has on the shelf unless an entire distribution package is being RFQ'd (e.g. switchboards, panels, transformers, etc). I wouldn't bother chasing a specific brand unless there's a good reason.
Member Jaref has a great post on 'Nominal System Voltage' vs 'Nominal Utilization Voltage':
For NEC load calculations in article 220.5 I use 416Y/240 as my 'Nominal System Voltage' feeders, panels and branch circuits also fault current calcs.
'Nominal Utilization Voltage' is 400Y/230 for 430.6(A) I use a custom table based on 400V 60HZ.
Noted. We're not in a rush to procure, so we had time to research brands.
Great info.
3-phase, 60Hz
480V primary
400V secondary
40kVA min.
Thanks!
Personally I dont care too much about what brand I get, its more about price, availability, and shipping. They are mostly all pretty much bullet proof. I bought one from these guys a year ago because they had it in stock and I needed it ASAP: