recptacles

Status
Not open for further replies.

bphgravity

Senior Member
Location
Florida
Re: recptacles

If you are refering to whether the receptacle should be mounted with ground pin up or ground pin down, there is no specification for either per NEC. Either way is compliant. If you mean the entire receptacle face up, this is allowed except for dwelling countertops or similar surfaces per 406.4(E).
 
G

Guest

Guest
Re: recptacles

I always install with the ground prong down so that that when a heavy cord assy is used and the plug starts to pull downward and out the last thing to be removed from the circuit is the ground prong.
 

james wuebker

Senior Member
Location
Iowa
Re: recptacles

You can put the ground up or down. I like the ground up. If you have it down then your Neutral & hot wire is on top. If your plug pulls out alittle then the N & the hot plong is expose. Something could slide down on it and cause a short circuit. If the ground pin was on top the item falling would hit the ground pin and fall off. No short curcuit. I have done it both ways.
Bye now,
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Re: recptacles

We all agree no position.

If all the appliances have the ground positioned so that the cord is going down when installed, could you say that if the ground was up it would put undue stress on the cord?

mp
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
Re: recptacles

Let us not forget neutral up or hot up. . .when the device is "sideways". All are possible orientations. And any other angle in the circle.
 

roger deas

Member
Location
North_Carolina
Re: recptacles

This covers it.

415i_diagram.jpg


Roger
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: recptacles

Thanks Roger. By the way those 4-in-one recptacles are a great application, and are less money than two recptacles in a two gang box, less labor as well.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: recptacles

Originally posted by bphgravity:
If you guys keep this up, we are going to have start using in-use covers on all receptacle outlets! :D

We could have the in use covers made with a switch to turn off the power when opened. :D

Roger,I think those outlets should be outlawed. ;)

How the heck are we going to ague over up or down with those dangerous outlets? ;)
 

cce

Member
Location
Alaska
Re: recptacles

Roger,
Do you rough that 4 plug device just on a 4sq box box? What is the mud ring for that guy? It shows like a #8 screw hole on all 4 corners, same config as 8/32 screws on a 4 sq.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: recptacles

CCE, it will work on a 4"sq, single, or double gang ring. There is a trim ring that is not shown for the latter two methods.

These are made in 15 and 20 amp, surge supression, isolated ground, and hospital grade.

You can go to the Hubbell or Bryant web sites for more info on these devices. Leviton makes a version of this also.

Hey Bob, I wouldn't fret to much, no matter what we come up with, this topic will be back again, and I promise I want show this dangerous device again. :D

Roger

[ March 22, 2003, 05:22 PM: Message edited by: roger ]
 