A recreational vehicle park has 20 sites. The sites are equipped with 20-ampere and 30-ampere supply facilities. The service will also consist of a building that will have a computed load of 90 amperes. The minimum feeder ampacity for the service conductors are:

3600va x 20 = 72,000 va x 45% (demand) =32,400 va / 240 volt = 135 amps + 90=225amp
The answer should be 279 amperes. what am i doing wrong? I also tried 125% of 90 amps but still no luck.

PLEASE HELP
thank you,
tacomafc
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I tried to approach it that 5% of all RV sites had to have a 50 amp supply, (555.71) so I tried adding one 50 amp with (20) 30 amp, also tried adding two 50's with (20) 30's, also tried reducing the 30s by the # of 50's.
Still could not get 279.
Perhaos someone will teach both of us something
 

jgunnels

Member
(try this )Recreational vehicle park

(try this )Recreational vehicle park

Just Learned how to do this several weeks ago.... I came up with 279amps.

first of all you have to take 20% (551.71 ) of the 20 sites at 9600va ( 4 )

then 70 % (551.71 ) of the 20 sites at 3600va ( 14 )

and the remainder (551.71 ) at 2400va ( 6 )

so what you end up doing is
4 x 9600 = 38,400
10 x 3600 = 36,000
6 x 2400 = 14,400
-------
88,800va / 240 volt then take 45% of this = 166.5amps ( 551.73 )
112.5
-------------
then add 125% of 90=112.5 amp 279.0 amps

hope this helps
 

jgunnels

Member
forgot to mention you count the first four of the 3600va in the 9600va
this is how you get the 10 x 3600va not 14 x 3600va
basicly it is implied that the first ( 4 ) 3600va are in the 9600va
hope i didn't confuse it more then it already is.
 