tacomafc
Senior Member
- Location
- Long Island New York
A recreational vehicle park has 20 sites. The sites are equipped with 20-ampere and 30-ampere supply facilities. The service will also consist of a building that will have a computed load of 90 amperes. The minimum feeder ampacity for the service conductors are:
3600va x 20 = 72,000 va x 45% (demand) =32,400 va / 240 volt = 135 amps + 90=225amp
The answer should be 279 amperes. what am i doing wrong? I also tried 125% of 90 amps but still no luck.
PLEASE HELP
thank you,
tacomafc
3600va x 20 = 72,000 va x 45% (demand) =32,400 va / 240 volt = 135 amps + 90=225amp
The answer should be 279 amperes. what am i doing wrong? I also tried 125% of 90 amps but still no luck.
PLEASE HELP
thank you,
tacomafc