Is it legal by code to use red and white as travelers on a 3 or 4 way switch?
Yes, but white conductor should be re-colored.Is it legal by code to use red and white as travelers on a 3 or 4 way switch?
Is it legal by code to use red and white as travelers on a 3 or 4 way switch?
Generally, with a string of switches, you would feed the far 3-way with the whites through the switch boxes, and use the red and black as the travelers, returning to the load on black, just like a 2-wire switch loop.Because of 200.7c1. Says reidentified white must be a supply. Which would be hot not a traveler correct?

Then how would you wire the switch on the right in the graphic?If the reidentified white is a traveler then it can not be a supply. Which the code states is mandatory. I believe you graffic is incorrect. The reidentified white would have to be used as the common of the 3way switch. Am I not correct in what the code is saying?
The code states... If used for single-pole, 3-way or 4-way switch loops, the reidentified conduc-tor with white or gray insulation or three continuous white or gray stripes shall be used only for the supply to the switch, but not as a return conductor from the switch to the outlet.
It must be a supply. I see the travelers being the return conductors because those are the wires that will be returning power to the switch leg. Is this not correct?