Has anyone found this supposed new 'requirement' that says all Fire Alarm Conduit shall be red???????
It could be a local requirement.
It could be a local requirement. Regardless, a call to the fire marshal whose town it is in would be in order since they're the one who's going to bless it or fail it.
Since the OP is in MA (the land of many fire alarm rules), that is a strong possibility.
No such rule and unenforceable anyway.
The requirement is that the boxes be identified.
I defer to the Master of Electricity. :roll:
I defer to the resident hack. :roll:
Just out of interest, do you guys ever use mineral insulated (MI) cable? Commonly called Pyro. It's used (with a red outer sheath) for fire protection systems.
Just out of interest, do you guys ever use mineral insulated (MI) cable? Commonly called Pyro. It's used (with a red outer sheath) for fire protection systems.
I've seen it used for that too. Emergency exit lights fed from a UPS in public buildings like cinemas.I have not used MI for fire alarm systems. We use either anything from PVC jacketed cables, to armored cables to conduits with cables or conductors used inside them.
These circuits are often loops and are wired and supervised in such a way that a single failure will only result in a notification of a problem that needs to be fixed while still having full functionality of the circuits.
Places I have used MI cables or other fire resistant cables are for line voltage supplies to emergency distribution panels or motors for things like smoke evacuation or building pressurization etc.
No such rule and unenforceable anyway.
The requirement is that the boxes be identified.
Just out of interest, do you guys ever use mineral insulated (MI) cable? Commonly called Pyro. It's used (with a red outer sheath) for fire protection systems.
You may well be right. It isn't my field but the ones I seen has been in MICC.FP cable has more or less taken the place of MICC. Running and making off MICC is a dieing art.
All kidding aside, I'm surprised to hear you say that. You're well aware that in MA and RI the fire departments can pretty much make up any rule they want with impunity. There is one town in my area that requires all smoke alarm boxes in new construction to be painted red. There's no written rule for this, but they require it anyway.