red leg service

Status
Not open for further replies.
Re: red leg service

red leg services that i am asken about, we see them at 120/240v warehouses, any help thank you
 
Re: red leg service

What do you need to know? If you are talking about 120/240 3 phase service, the neutral for the 120's is made by tapping the center of one transformer secondary in a delta connected bank of 2 or 3 power co. transformers. This results in the "red" leg which is around 208 volts measured to the neutral. Voltage is 240 between any two legs and it is true 3 phase if you use all 3.

Jim
 
Re: red leg service

One of the better books around about transformers is by Tom Henry; Transformer calculations. It is a part of my library.

The "high leg" is 208v to neutral or ground on a 120/240v 3 Phase, 4 wire delta connected transformer. The high leg is calculated by the formula 120 volts x square root of 3 = 208 volts.

These are widely used in commercial and industrial applications.

I haven't really looked at this edition of the NEC to see if a change in the code was made concerning the high leg located in a panel that did not supply 3 phase loads. If it wasn't changed, it needs to be.

The NEC requires the high leg be B phase and colored orange. 110.15, 408.3(E),
 
Re: red leg service

Although it results in the same answer, the high leg to neutral voltage is actually calculated as shown below.

4Wdelta2.gif


concerning the high leg located in a panel that did not supply 3 phase loads. If it wasn't changed, it needs to be.
We are now required to install a separate panel for the single phase loads.

Trans14.gif


Ed
 
Re: red leg service

Originally posted by edavis2293:
Where in the NEC is the requirement for a separate panel if we have line-to-neutral loads. I have been looking for it.
I don't believe there is such a rule.

What would be the need for the rule, 110.4 already covers it. :)
 
Re: red leg service

Ed,
The square root of three works because the tangent of 60 degrees is equal to the square root of 3. The tangent of an angle in a right triangle is equal to opposite/adjacnet.
tan60=x/120
tan60=square root of 3
(square root of 3)(120)= x
x=high leg voltage
 
Re: red leg service

Sorry, edavis2293, I should have been more specific. I was referring to one of our local requirements.

Ed
 
Re: red leg service

Originally posted by Ed MacLaren:
Sorry, edavis2293, I should have been more specific. I was referring to one of our local requirements.
Ed
Ed what do you think of this rule?

Shouldn't a qualified person know how to feed a line to neutral load from a high leg panel?
 
Re: red leg service

Shouldn't a qualified person know how to feed a line to neutral load from a high leg panel?
Yes, I agree.

But, we both know that there are unqualified people doing electrical work, right? :(

I remember an incident that happened to a couple of my co-workers. They were installing a three phase motor at a local dairy, and when connecting to the panel, they discovered that, although there was no three-pole spaces available, there were a number of single-pole spaces.

So, they moved some single pole breakers up into those empty spaces to make room for their new three-pole breaker.

You can guess the result.

Ed
 
Re: red leg service

Yes.

To my knowledge there is no three phase unit available that can be loaded more than 5% @ 120V. This is because of a single (common) core.

Most 240/120 high-leg systems are made up of two or three single phase units.
 
Re: red leg service

By Jim D: To my knowledge there is no three phase unit available that can be loaded more than 5% @ 120V. This is because of a single (common) core.
Wouldn't that only apply to an open delta?
A closed delta can be 57% out of balance?
I'm not sure if I got this right. :confused:
 
Re: red leg service

Wayne,
Jim is talking about a 3 phase transformer on a single core. You are are talking about a 3 phase bank made up of two or three single phase transformers.
Don
 