One of the better books around about transformers is by Tom Henry; Transformer calculations. It is a part of my library.
The "high leg" is 208v to neutral or ground on a 120/240v 3 Phase, 4 wire delta connected transformer. The high leg is calculated by the formula 120 volts x square root of 3 = 208 volts.
These are widely used in commercial and industrial applications.
I haven't really looked at this edition of the NEC to see if a change in the code was made concerning the high leg located in a panel that did not supply 3 phase loads. If it wasn't changed, it needs to be.
The NEC requires the high leg be B phase and colored orange. 110.15, 408.3(E),