Re: Red tags and more Red tags
Thank's Don I wasn't thinking (as usual) :roll:
Pierre:
If they are both installed using a single receptacle and on the same circuit, the single receptacles are now two receptacles on the same circuit, so 210.21(B)(1) does not pertain to this installation.
How is this when 210.21(B)(1)says:
Where connected to a branch circuit supplying two or more receptacles or outlets ,
It doesn't say that single receptacles wouldn't count? It means two or more receptacles on the circuit, and two single receptacles would be two or more wouldn't it?
The other question is, 250.146 allows for the device to be grounded to the box through the yoke if the box is surface mounted and if at least one of the screw retainer washers is removed to allow direct metal to metal contact. And if the box is flush mounted then the receptacle has to have a contact device that maintains continuity on the screw as in a self grounding receptacle.
With that said if you used a short section of conduit to run down a basement wall to a handy box, and the EGC in the circuit cable is connected to the receptacle terminal. would the reverse also apply since the grounding conductor is now connected to the receptacle first will 250.146 allow the receptacle yoke to bond the box and conduit as 250.148 requires? 250.148 doesn't seem to allow it, and I don't understand why? It's like the bonding of the box and conduit is more important than the bonding of the receptacle.
And for the last question:
The requirement of bonding between the cold and hot water pipes at the water heater?
Now this is the first time that we have had an inspector in this area require this, and it's been a long time that I was ever required to make this bond.
I know we have talked about this before but it was awhile back and I think because most dwellings today will have one or more points of connection (mixing valves) between the hot and cold water pipes that a bond at the water heater is unnecessary. But I could see this call in a commercial environment as few will have these connections if only it has simple sinks that are connected by plastic hoses. restaurants will have this connection because of the health boards requirement to have the bathroom sink hot water temperature at 120 degs. and the wash temp at 160 degs. this would require a mixing valve unless two water heaters were used.
I would just like some input on this before I approach the inspector.
Just to let you know, and I know Charlie E. has mention it many times also. Here in Indiana a local unit of government is not allowed to make up his own rules. And Indiana has even removed 90.4 from Indiana's electrical code putting in it's place the state IC code requirement that any variance to the IEC has to be accepted by the state building commissioners before it can be adopted as a local code. So they have to go by what is in the IEC as verbatim because any changes will be in there.
Thank's for every's one's help as I really appreciate it.