3.3.8 Pressurization. The process of supplying an enclosure with a protective gas with or without continuous flow at sufficient pressure to prevent the entrance of a flammable gas or vapor, a combustible dust, or an ignitable fiber.3.3.8.1 Type X Pressurizing. Reduces the classification within the protected enclosure from Division 1 or Zone 1
to unclassified.
3.3.8.2 Type Y Pressurizing. Reduces the classification within the protected enclosure from Division 1 to Division 2 or Zone 1 to Zone 2.
3.3.8.3 Type Z Pressurizing. Reduces the classification within the protected enclosure from Division 2 or Zone 2 to unclassified.
Sometimes nitrogen is specified because it is relatively easy and not outrageously expensive to put a bottle of nitrogen out where the panel is. Its not required for reducing the classification, but might be handy for other reasons.jaykool said:Can someone provide a Type X or Type Z Pressurizing example (is nitrogen gas used)?
petersonra said:Sometimes nitrogen is specified because it is relatively easy and not outrageously expensive to put a bottle of nitrogen out where the panel is. Its not required for reducing the classification, but might be handy for other reasons.
BTW, has anyone here ever actually used type Y? I never have, and can't even ever recall seeing it.
weressl said:Analyzers is one example where you actually carry the flammables inside the analyzer cabinet and need to expose them to be analyzed, so you purge the cabinet to keep it below LFL.
petersonra said:what does that have to do with nitrogen purging?
are you saying you purge with N2 so there is no oxygen inside the cabinet that might potentially react with the flammables?
never had to do that although I seem to recall one panel that was purged had the exhaust piped to a non-hazardous area so the solenoid valves could exhaust inside the box and have no path for hazardous gases to enter through the exhaust tubing.