Reduce Classification within a Protected Enclosure

Status
Not open for further replies.

jaykool

Member
Location
NE
At the end of 500.7 (Protection Techniques) it talks about pressurized enclosures to reduce classification. Can someone explain what Type X, Type Y, and Type Z pressurizing mean? What is the difference between X and Y?
 
It is fairly straight-forward. From NFPA 496-2003, Standard for Purged and Pressurized Enclosures for Electrical Equipment:

3.3.8 Pressurization. The process of supplying an enclosure with a protective gas with or without continuous flow at sufficient pressure to prevent the entrance of a flammable gas or vapor, a combustible dust, or an ignitable fiber.
3.3.8.1 Type X Pressurizing. Reduces the classification within the protected enclosure from Division 1 or Zone 1
to unclassified.
3.3.8.2 Type Y Pressurizing. Reduces the classification within the protected enclosure from Division 1 to Division 2 or Zone 1 to Zone 2.
3.3.8.3 Type Z Pressurizing. Reduces the classification within the protected enclosure from Division 2 or Zone 2 to unclassified.


 
NFPA 496 is the recognized Standard for Purged and Pressurized Enclosures for Electrical Equipment. The link is to the NFPA’s 2008 online edition.

There are several considerations for each “Type.” They are generally outlined in Chapters 4 and 5. “Additional Requirements for Type Y or Z Pressurizing” are reviewed in Section 5.4. “Additional Requirements for Type X Pressurizing” are reviewed in Section 5.5. Chapter 8 contains information where the enclosures have an internal source of flammable gas or vapors.

Nitrogen is a common “protective gas,” although it is not specifically required in any particular application. It is commonly considered to be an inert gas in the few applications that require that property, especially if it is of the "Dry" type. ("Dry" is NOT a requirement in itself though, just generally considered good practice.)

Without specific knowledge of the anticipated installation, it is impossible to say much more.

Edit Spelling
 
Last edited:
jaykool said:
Can someone provide a Type X or Type Z Pressurizing example (is nitrogen gas used)?
Sometimes nitrogen is specified because it is relatively easy and not outrageously expensive to put a bottle of nitrogen out where the panel is. Its not required for reducing the classification, but might be handy for other reasons.

BTW, has anyone here ever actually used type Y? I never have, and can't even ever recall seeing it.
 
petersonra said:
Sometimes nitrogen is specified because it is relatively easy and not outrageously expensive to put a bottle of nitrogen out where the panel is. Its not required for reducing the classification, but might be handy for other reasons.

BTW, has anyone here ever actually used type Y? I never have, and can't even ever recall seeing it.

Analyzers is one example where you actually carry the flammables inside the analyzer cabinet and need to expose them to be analyzed, so you purge the cabinet to keep it below LFL.
 
weressl said:
Analyzers is one example where you actually carry the flammables inside the analyzer cabinet and need to expose them to be analyzed, so you purge the cabinet to keep it below LFL.

what does that have to do with nitrogen purging?

are you saying you purge with N2 so there is no oxygen inside the cabinet that might potentially react with the flammables?

never had to do that although I seem to recall one panel that was purged had the exhaust piped to a non-hazardous area so the solenoid valves could exhaust inside the box and have no path for hazardous gases to enter through the exhaust tubing.
 
petersonra said:
what does that have to do with nitrogen purging?

are you saying you purge with N2 so there is no oxygen inside the cabinet that might potentially react with the flammables?

never had to do that although I seem to recall one panel that was purged had the exhaust piped to a non-hazardous area so the solenoid valves could exhaust inside the box and have no path for hazardous gases to enter through the exhaust tubing.

My response was given to the Y purging.

Nitrogen can be used for purging where inerting may simplify the classification issue. If nitrogen used then the classification would be X, not Y.
 