Re: Reduce neutral for non-linear loads
You should take a look at 220.22 Feeder or Service Neutral Load.
Here is part of it.
There shall be no reduction of the neutral capacity for that portion of the load that consists of nonlinear loads supplied from a 4-wire, wye-connected, 3-phase system.
A good portion of our jobs are in buildings with many non-linear loads, I have never seen an engineer reduce the neutral size on anything.
About half the time the neutral is
doubled in size and the panel has a 200% rated neutral bar.
A 225 amp panel would have one 4/0 for A, B & C and two 4/0s for the Neutral.
I believe this is one of the reasons for the exception to 408.21
408.21 Grounded Conductor Terminations.
Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.
Exception: Grounded conductors of circuits with parallel conductors shall be permitted to terminate in a single terminal if the terminal is identified for connection of more than one conductor.