OK, Here's my situation:
Service Voltage is 120/208, 3 ph, 4W.
Service to Dwelling is 120/208, 1 ph, 3W
I have 1248 SF apartment with the following appliances:
(2) appliance Circuits
(1) 8800W Range
(1) 744W Dishwasher
(1) 3928W Stacked Washer/Dryer (single outlet)
(1) 1200W AHU blower
(1) 5625W Heating Element
Calculating the Service according to 220.30 I came up with a 95 Amp service. What is the min. neutral conductor allowed by 220.22?