I want to double check my sanity:
Singel phase Line-Line loads don't cause any current to flow on the neutral, right?? And if I have 6 L-L loads, all connected to different combinations of phases, there still won't be any neutral current, no matter what combination of loads are on or off at any time, right again??
I'm still trying to fit a 400A feeder into an existing 3" conduit (208v, 3 phase service). The total calculated load is 137 KVA, but only 35KVA is for lighting and receptacles. The other 102KVA is all 208V Line-Line HVAC loads (most of that is 10KW electric heaters).
I am thinking I can reduce the neutral size to about 250A. So I would have (3) x 500KCM, a 250KCM neutral, and a #3 ground from the service disonnect to the main panel.
Steve
Steve