Does Article 220.22 prohibit reduction of neutral conductor to a multifamily dwelling unit that is being served with 120/208 Volt single phase service?
In some areas it is common for a dwelling unit service to be fed with two phases and the grounded conductor from a 208/120 volt 4 wire wye system.120/208 Single phase??????
Just a question, but what happened to the other loads in the house...ie refrig, convience outlets, computers, lighting, and other miscellaneous loads?Originally posted by jpmccleery:
posted July 14, 2004 01:25 PM
--------------------------------------------------------------------------------
OK, Here's my situation: I have 1248 SF apartment with the following appliances:
(2) appliance Circuits
(1) 8800W Range
(1) 744W Dishwasher
(1) 3928W Stacked Washer/Dryer (single outlet)
(1) 1200W AHU blower
(1) 5625W Heating Element
Calculating the Service according to 220.30 I came up with a 95 Amp service. What is the min. neutral conductor allowed by 220.22?
You have to use the larger of what is required by 220.22 or 250.24(B)(1).when you have those loads calculated, then you use 250.66 and size your neutral, based on you other phase conductors.
See 220.3(B)(10).The 3VA per foot would just be lighting.
I think if you would show the calculations you used to get this figure it would be easier for someone to help you with your question.Calculating the Service according to 220.30 I came up with a 95 Amp service
I'm not surprised by a dispute from Don, once again. I seem to always be his target.Originally posted by don_resqcapt19:
Lady,
You have to use the larger of what is required by 220.22 or 250.24(B)(1).when you have those loads calculated, then you use 250.66 and size your neutral, based on you other phase conductors.
See 220.3(B)(10).The 3VA per foot would just be lighting.
Don
Notice that items 1, 2 and 3 are for the receptacle outlets being discussed. Also, what value would you assign these receptacles? The 180VA provision is pretty specific when it says that it does not apply to dwelling units.220.3(B)(10)(10) Dwelling Occupancies. In one-family, two-family, and multifamily dwellings and in guest rooms of hotels and motels, the outlets specified in (1), (2), and (3) are included in the general lighting load calculations of 220.3(A). No additional load calculations shall be required for such outlets.
(1) All general-use receptacle outlets of 20-ampere rating or less, including receptacles connected to the circuits in 210.11(C)(3)
(2) The receptacle outlets specified in 210.52(E) and (G)
(3) The lighting outlets specified in 210.70(A) and (B)
Ok, I see...thanks Ryan.Originally posted by ryan_618:
Back to the original question really quick. Remember that on a three wire circuit supplied by a four wire system, the nuetral carries a lot of current. For example, if you have 100 amps on phase "A", 100 amps on phase "B" and zero amps on phase "C", you will have 100 amps on the nuetral. This can be proven by the following formula:
Total nuetral current= The sqaure root of the following: (A squared+ B sqaured+ C sqaured)-(AB+BC+CA).
In my example, you would take the sqare root of: (10,000 + 10,000 + 0) - (10,000 + 0 + 0), which eqauls the sqaure root of 10,000= 100 amps on the nuetral...that is why no reduction is permitted.
Lady: Don is right.Notice that items 1, 2 and 3 are for the receptacle outlets being discussed. Also, what value would you assign these receptacles? The 180VA provision is pretty specific when it says that it does not apply to dwelling units.220.3(B)(10)(10) Dwelling Occupancies. In one-family, two-family, and multifamily dwellings and in guest rooms of hotels and motels, the outlets specified in (1), (2), and (3) are included in the general lighting load calculations of 220.3(A). No additional load calculations shall be required for such outlets.
(1) All general-use receptacle outlets of 20-ampere rating or less, including receptacles connected to the circuits in 210.11(C)(3)
(2) The receptacle outlets specified in 210.52(E) and (G)
(3) The lighting outlets specified in 210.70(A) and (B)
Ryan, can you address this question, please?If what you are saying is true , then why in Annex D, Examples D5(a) and (b) a calculation for reducing the neutral is provided?
From what I can see in the examples, the only nuetral reduction used is for the range. This is specifically allowed in 220.22 for all ranges. I beleive this is because, as you would agree, the nuetral doesn't do much on a range. In fact, there are probably ranges out there that don't even use a nuetral. The way I read 220.22 is this: Ranges are subject to nuetral reduction...always. I think that section is poorly written and needs the verbage re-arranged in the section. I think that, other than for ranges and dryers, you cannot reduce the nuetral capacity on a three wire feeder supplied by a four wire service.Originally posted by wirebender:
Ryan, can you address this question, please?If what you are saying is true , then why in Annex D, Examples D5(a) and (b) a calculation for reducing the neutral is provided?
Remember that on a three wire circuit supplied by a four wire system, the nuetral carries a lot of current. For example, if you have 100 amps on phase "A", 100 amps on phase "B" and zero amps on phase "C", you will have 100 amps on the nuetral
On the range you probably have about 3 amps of 120-V load. So, doing the formula, you have the sqaure root of: (9+0+0)-(0+0+0)=3 amps.Originally posted by wirebender: