Re: Reduced Neutral
Patty,
First off, the original question asked about a reduced neutral in 220v single phase service.
Second, even with computers, HID lightning and other nonlinear loads, there is no problem with high neutral currents on 120/240 volt 3 wire single phase systems. That is a system that originates from a 120/240 volt single phase transformer. The harmonic currents do not add in the neutral on a single phase system like they do in 3 phase systems. If I was designing the electrical system for a facility where nonlinear loads were expected to be a major portion of the load, I would use 120/240 single phase for the panels that serve these types of loads. Of course, unless there are a number of 240 volt loads, the neutral serving a 120/240 volt single phase panel will have to be the same size as the hots, but there would be no reason to install an oversized neutral. Even if the service is 480/277 wye, you could use single phase 480 to 120/240 transformers to serve these loads. We don't hear much about using 120/240 single phase as a solution for the high neutral current problem. I wonder if that is because there is more profit in installing harmonic filters, harmonic blockers, K rated transformers and upsized neutrals.
Don