W wire4u73 Member Jan 24, 2011 #1 What are the stipulations for reducing the neutral conductor and is there a certain percentage that it cannot be reduced past?
What are the stipulations for reducing the neutral conductor and is there a certain percentage that it cannot be reduced past?
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Jan 24, 2011 #2 220.61 is where I would start.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jan 24, 2011 #3 220.61 gives you the basics. If it's a feeder neutral, 215.2 gives you a minimum (sorry jumper, stepped on you) Last edited: Jan 24, 2011
220.61 gives you the basics. If it's a feeder neutral, 215.2 gives you a minimum (sorry jumper, stepped on you)
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Jan 24, 2011 #4 For a service look at 250.24(C)(1)