I am looking at an existing existing 4000A service that has 10 sets of 500MCM cables however the neutrals are only 10 sets of 4/0 cables. This is an older installation and now that the main switchboard is being replaced I'm wondering if larger neutral's have to be run with the existing 10 sets of 500MCM feeders?
I was always under the impression that the NEC required neutral to be same size as phase conductors however there were articles that allowed for using a smaller neutral. NEC 250.24 comes to mind.
Can someone tell me what is required for service entrance neutral conductors and what sections can be applied for using a reduced neutral. Does a reduced 4/0 neutral sound right for this instance?
Thanks