Reduced size ground wire in NM?

Status
Not open for further replies.

mlnk

Senior Member
Is the ground wire in NM smaller than the black and white wire? I know that years ago it was, but is that the case now? I am asking because this is mentioned in the FAQ in this NEC forum.
 
Is the ground wire in NM smaller than the black and white wire? I know that years ago it was, but is that the case now? I am asking because this is mentioned in the FAQ in this NEC forum.
The egc is the same size as the conductors in sizes 14-10. Once you get higher then that the sizes change to match, hopefully with 250.122. This can be a problem when upsizing for VD as the EGC may not change depending on the wire sizes.
 
MN in sizes 14, 12, and 10 has had a full sized EGC (in the NEC world) since the late 60's or very early 70's.
 