I have a burning question about vintage NM cable with reduced-size grounding/bonding wires.
We recently encountered cable with 12AWG white & black wires and 16AWG bare, protected by 20-amp Pushmatic breakers. If my calculation is correct -- and this is what I'd like the larger community to confirm or deny -- it would be possible for there to be a 500oC temperature rise in the grounding/bonding wire while the breaker carries 200% for two minutes.
Here's what I started with:
16 AWG copper wire:
- 0.0132 ohms per meter
- 0.00129 meter diameter
- 8920 kg per m3 density
- 385 kJ per kg·Kelvin thermal capacity
- 1083 oC melting point
20-amp breaker worst-case let-through current:
- 40 amps (200%) for two minutes (is this the worst-case I2t?)
And here's what I calculated:
- 1.31x10-6 m2 cross-section
- 0.0117 kg per meter
- 21.1 watts per meter
- 2530 Joules per meter (2 minutes)
- and an adiabatic temperature rise of 563 oC during a worst-case hot-to-ground bonded fault.
First of all, are my calculations correct & relevant?
Second of all, what, if anything, ought to be done about it? Shrug it off as capable of withstanding a worst-case fault without melting, knowing that the cable insulation will be damaged? Replace the 20-amp breakers with 15? Add 12AWG grounding/bonding wires?
We recently encountered cable with 12AWG white & black wires and 16AWG bare, protected by 20-amp Pushmatic breakers. If my calculation is correct -- and this is what I'd like the larger community to confirm or deny -- it would be possible for there to be a 500oC temperature rise in the grounding/bonding wire while the breaker carries 200% for two minutes.
Here's what I started with:
16 AWG copper wire:
- 0.0132 ohms per meter
- 0.00129 meter diameter
- 8920 kg per m3 density
- 385 kJ per kg·Kelvin thermal capacity
- 1083 oC melting point
20-amp breaker worst-case let-through current:
- 40 amps (200%) for two minutes (is this the worst-case I2t?)
And here's what I calculated:
- 1.31x10-6 m2 cross-section
- 0.0117 kg per meter
- 21.1 watts per meter
- 2530 Joules per meter (2 minutes)
- and an adiabatic temperature rise of 563 oC during a worst-case hot-to-ground bonded fault.
First of all, are my calculations correct & relevant?
Second of all, what, if anything, ought to be done about it? Shrug it off as capable of withstanding a worst-case fault without melting, knowing that the cable insulation will be damaged? Replace the 20-amp breakers with 15? Add 12AWG grounding/bonding wires?