Reduced-size grounding/bonding wire in vintage NM cable

Status
Not open for further replies.

drcampbell

Senior Member
Location
The Motor City, Michigan USA
Occupation
Registered Professional Engineer
I have a burning question about vintage NM cable with reduced-size grounding/bonding wires.

We recently encountered cable with 12AWG white & black wires and 16AWG bare, protected by 20-amp Pushmatic breakers. If my calculation is correct -- and this is what I'd like the larger community to confirm or deny -- it would be possible for there to be a 500oC temperature rise in the grounding/bonding wire while the breaker carries 200% for two minutes.

Here's what I started with:
16 AWG copper wire:
- 0.0132 ohms per meter
- 0.00129 meter diameter
- 8920 kg per m3 density
- 385 kJ per kg·Kelvin thermal capacity
- 1083 oC melting point
20-amp breaker worst-case let-through current:
- 40 amps (200%) for two minutes (is this the worst-case I2t?)

And here's what I calculated:
- 1.31x10-6 m2 cross-section
- 0.0117 kg per meter
- 21.1 watts per meter
- 2530 Joules per meter (2 minutes)
- and an adiabatic temperature rise of 563 oC during a worst-case hot-to-ground bonded fault.

First of all, are my calculations correct & relevant?
Second of all, what, if anything, ought to be done about it? Shrug it off as capable of withstanding a worst-case fault without melting, knowing that the cable insulation will be damaged? Replace the 20-amp breakers with 15? Add 12AWG grounding/bonding wires?
 

jumper

Senior Member
Reduced EGCs for small branch circuits was legal until the '68 or '71 code.

If you do not modify the circuit, you do not have to do anything.

If you wish to upgrade, a proper sized EGC will be needed.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
When you ask 'what ought to be done about it', are you asking what is mandated by code, or has the decision already been made to 'fix' this and you are asking what the best method is to fix it?

1) Your calculation is a reasonable approximation.

It is very unlikely that you will have a fault that is just the worst maximum that the breaker will carry, and the resistance will change substantially as the wire heats up, so any fault current is likely to change.

2) As what _should_ be done, code changed to prohibit these reduced size conductors. Clearly the design is not 'safe enough' for current code, but was considered 'safe enough' to grandfather. That is probably all that should be mandated.

3) If a design choice is made to 'fix' this issue, I would either replace the NM with new, or replace the breakers with something that offers ground fault detection. I would not run extra bonding wires; the effort (labor cost) to run such wires is similar to the effort to run new cables, and the materials cost is not much less.

-Jon
 