Reduced voltage motor starting

Status
Not open for further replies.

tweekster

Member
I recently came across a problem of a six lead 3 480 volt 300 HP 340 FLA with the option of an in-line delta connection or a Y-start/delta run configuration motor which powers an Ammonia based compressor for an IQF system at a food processing plant, not wanting to start. Couple minutes of troubleshooting, find that the third leg of a Square-D thermal-magnetic 600V 600A 3 pole circuit breaker with the Mag adjust setting at aprox. 4500A had burned up. A little puzzled, replaced the breaker in order to get the system back up and running. Compressor started, and the system seemed to be running just fine. Started investigating for answers to report to the customer why this $3400.00 (my cost used) breaker had burned up and how to prevent it from happening again. Here's my findings after talking to maintenance personell, visual inspection, studying schematics, and personal knowledge.
Breaker would trip aprox. 4-5 times a month 95% of the time with in 3 sec. of start up. Maintenance personell would just reset it and the system would start the second time until the breaker would give up. Well, answer about the breaker. Also found out that this was the fourth breaker in about 3 yrs. Here's what else I found. It was a clean professional installation. Top of the line SQUARE-D Equipment from the 3000A 480V Distribution through the size 6 which I at first thought was a Y-start/Delta Run set up, 600KMCM copper conductors all controlled by a computer based controller/diagnostic set up on the compressor. Visual inspection of the motor revealed some winding dark in color and apparent insulation break down. Megger confirmed this. OK. Motor degrading this could be the cause of the breaker tripping. Now, why motor degregation. At this point, customer wanted to replace the motor in order to prevent any system down time. (New motor $7000.00 my cost) Time to find out how to prevent reoccurence. Further investigation of the starting cabinet. It's premanufactured by SQURE-D consisting of 3 size 6 starters, a tapped off thermal overload set up, a couple of timing relays, mechanical interlocks between starters, CT on center leg for computer etc.. Wasn't to sure why only three conductors to motor or what the fairly good sized xfmer at the bottom of the cabinet was for. Read schematics and found out that it was a reduced voltage starter set up which is the first time I ever came across something like this. So here's the questions I have for you guys.
1) Why this kind of set up when the motors designed for Y-start/Delta run and all you would really need is three more conductors if you needed a high torque start?
2) If I can turn the shaft of the motor while connected to the load by hand, why not just a regular delta connection?
3) What the heck is the purpose of a reduced voltage start where the xfmer is tapped at 65% of line voltage at start up? Are'nt most motors tolorences with in 20% before damage may occur? Wouldn't the reduced voltage create excessive current and heat to the windings of the motor causing insulation breakdown over a period time to the point of excessive in rush current applied to protective device such as a breaker bypassing the thermal overload protection.
4) Any comments, thoughts, or solutions would be appreciated.
By the way, I called the tech. assist line of the motor manufacturer and asked basically the same questions, but directing it towards what affect and concerns it has on the motor, and I couldn't really get a direct answer. Thanx, Bill

[Moderator's Note: Edited to remove email address.]

[ July 15, 2004, 09:50 AM: Message edited by: charlie b ]
 
Re: Reduced voltage motor starting

Your description sounds like an Auto-transformer Starter to me. (example sketch below)

These normally have 50%, 65%, and 80% taps on the transformer. The starting torque is directly affected by the tap selected.
It would be nice to know the starting inrush current to determine if the correct tap is being used.

Here are a couple of links to some technical info-

Reduced Voltage Starting

Square D catalog info

Ed

AutoTran4.gif
 
Re: Reduced voltage motor starting

Reduced voltage start is used when the load cannot handle the starting torque of the motor, or sometimes if the electrical system is not "stiff" enough and you want to minimize voltage dips during starting.

Autotransformer starters give you a choice of 50%, 65% or 85% starting voltage, which gives you a corresponding 50/65/85% current. The torque is the voltage squared, or 25/42/64% torque to the load.

Y-Delta starters only give you one choice - 58% voltage which is 33% torque.

The manufacturer may have felt that 33% wouldn't be sufficient. Or the engineer may have wanted more options just in case. :) Or maybe someone got a "deal" on the autotransformer starter being available sooner. Who knows... ?
 
Re: Reduced voltage motor starting

One of the biggest reasons that I know for using reduced starting motor is to lower the electric bill. this was one of the reasons 12 lead motors came about. Almost all industrial plants and many commercial buildings use peek demand meters. Reducing start up torque in the right way also reduces startup current thus reducing the peek demand. If you were to read the current when a regular 3-phase motor started it will be close to locked rotor amps. but with reduced torque motors this is reduced to about 1/3 this. Even though with the full startup torque it will be for a shorter period of time, the peek demand meter didn't care it still moved the peek hand up to this high current peek. The other way we used to combat this is to sequence the motors and use soft starts.
 
Re: Reduced voltage motor starting

Originally posted by hurk27:
One of the biggest reasons that I know for using reduced starting motor is to lower the electric bill. this was one of the reasons 12 lead motors came about. Almost all industrial plants and many commercial buildings use peek demand meters. Reducing start up torque in the right way also reduces startup current thus reducing the peek demand. If you were to read the current when a regular 3-phase motor started it will be close to locked rotor amps. but with reduced torque motors this is reduced to about 1/3 this. Even though with the full startup torque it will be for a shorter period of time, the peek demand meter didn't care it still moved the peek hand up to this high current peek. The other way we used to combat this is to sequence the motors and use soft starts.
That's a new one on me. Demand meters usually average the demand over a 15 or 30 minute period. I wouldn't think that the starting KVA lasting a few seconds would move the demand up enough to consider demand billing cost savings vs. the cost of the reduced voltage starter/motor.
 
Re: Reduced voltage motor starting

Since I posted this, I've done alot of research on this and learned quite a bit. There is one thing that still puzzles me, and I can't seem to find an answer on what affect this has on the motor which isn't really designed to operate beyond it's specs, especially at start, up for a period of time.
 
Re: Reduced voltage motor starting

There is one thing that still puzzles me, and I can't seem to find an answer on what affect this has on the motor
It is easier on the motor. The reduced inrush current results in less thermal stress on the windings, as well as less mechanical stress on bearings, couplings, and other drive components.

Ed
 