When entering enclosures required to be flameproof or explosionproof in a Class 1 Zone 2 locations using a cable seal, are you allowed to use more than one listed explosionproof reducer?
 
When entering enclosures required to be flameproof or explosionproof in a Class 1 Zone 2 locations using a cable seal, are you allowed to use more than one listed explosionproof reducer?
Yes. There is no restriction for reducers between the seal and the enclosure for wiring methods that are consistent with Zone 2.
 