PE (always learning)
Senior Member
- Location
- Saint Louis
- Occupation
- Professional Engineer
I have a power systems study that I'm doing for a data center and they are trying to figure out ways to reduce the arc flash incident energy below 40 cal/cm^2 at certain panel locations so that they can work on equipment live with the proper PPE. One such way that I can decrease the arc flash incident energy is by running everything through the generator instead of through the utility. This data center does not utilize generators in parallel, so the fault current produced by this generator is substantially lower than what is produced by the utility source. Normally this would be an issue for over current protection clearing times, but this decrease in fault current when being fed by the generator actually worked in my favor for this project and made the incident energy lower than 40 cal/cm^2 on the secondary side of a large transformer that feeds my panel in question. Would it be ok to allow the facility to work on certain panels live when running the generator ONLY? Again, I know that working on things live should never really be an option, but I'm trying to work with them here.